How to reduce the mismatch after doing OPF?
I am doing OPF with loss reduction(active & reactive) as the objective, and my control are round switched shunt and transformer tap ratios
But after that, the report shows that my system mismatch is large = 30~40MVA, i'm wondering know how to reduce the mismatch after doing OPF?
thanks!
Isn't it just to solve the network?
So you mean i don't really need to care about the system mismatch?
Have you made a normal load flow calculation with FNSL?
Yes, if I run the normal load flow calculation with FNSL after OPF, the mismatch will be declined. So is it normal with a large mismatch after OPF?
My steps are : first :made the subsystem doing OPF with loss reduction(active & reactive) →mismatch:30~40MVA second:if i run a normal load flow calculation with FNSL →mismatch<0.1MVA I think the second step will loss the objective, although it made the system balance.