How to reduce the mismatch after doing OPF?

asked Apr 8 '0

Crash gravatar image

I am doing OPF with loss reduction(active & reactive) as the objective, and my control are round switched shunt and transformer tap ratios

But after that, the report shows that my system mismatch is large = 30~40MVA, i'm wondering know how to reduce the mismatch after doing OPF?

thanks!

Comments

Isn't it just to solve the network?

perolofl gravatar imageperolofl (Apr 8 '0)

So you mean i don't really need to care about the system mismatch?

Crash gravatar imageCrash (Apr 8 '0)

Have you made a normal load flow calculation with FNSL?

perolofl gravatar imageperolofl (Apr 8 '0)

Yes, if I run the normal load flow calculation with FNSL after OPF, the mismatch will be declined. So is it normal with a large mismatch after OPF?

Crash gravatar imageCrash (Apr 8 '0)

My steps are : first :made the subsystem doing OPF with loss reduction(active & reactive) →mismatch:30~40MVA second:if i run a normal load flow calculation with FNSL →mismatch<0.1MVA I think the second step will loss the objective, although it made the system balance.

Crash gravatar imageCrash (Apr 8 '0)