PSSE V32, PQ Mismatch Between Pelec/Qelec and Flow(Q+P)

Hey guys, I am using PSSE V32 to run a dynamic fault study however there seems to be a significant mismatch between Pelec/Qelec and Flow(Q+P) outputs. For example in this case there is an inverter at bus 903 and after the fault the Pelec/Qelec go back to values that are expected, however the Flow(Q+P) to the bus it is connected to 901 are quite different. Any help would be appreciated, Thanks image description

haveityourwa's avatar
25
haveityourwa
asked 2017-09-29 01:09:41 -0500, updated 2017-09-29 01:11:06 -0500
edit flag offensive 0 remove flag close merge delete

Comments

Is there any more equipment connected to bus 903?

perolofl's avatar perolofl (2017-09-30 01:58:27 -0500) edit

The only equipment connected to bus 903 is the Generator and the transformer to bus 901

haveityourwa's avatar haveityourwa (2017-09-30 02:03:22 -0500) edit
add a comment see more comments

1 Answer

0

It appears as though there was an issue with the inverter model. However if someone could explain the difference between Qelec/Pelec and Q + P flow that would be appreciated however for now this issue is resolved.

haveityourwa's avatar
25
haveityourwa
answered 2017-10-18 18:38:08 -0500
edit flag offensive 0 remove flag delete link

Comments

Pelec & Qelec values are in pu of system base (=100) and to get true values, just multiply their values by 100. After doing that, Pelec = Flow P. Qelec + Qloss at bus 903 (=transformer admittance) = Flow Q