Hi guys Can anyone tell me how to force P&Q limit in PSSE please. I want the PSSE not to go over the maximum P&Q limit in power flow or dynamic simulation.

Thanks in advance

2 answers

Sort by » oldest newest most voted
0

answered Dec 10 '19

perolofl gravatar image

The maximum limit in the governor model (e.g. Pmax,gmax, etc) should be set to a value corresponding to the Pmax limit used in load flow.

link
0

answered Dec 5 '19

jfconroy gravatar image

For power flow studies, check out the GCAP function. In dynamic simulations, you have to build the logic into your AVR model.

link

Comments

Thanks jfconroy !

KF gravatar imageKF (Dec 6 '19)