Ask Your Question
0

Short Circuit Current Use psse dynamic simulation and IEC module (psse34)

asked 2018-10-16 22:31:26 -0500

Gloria.Z gravatar image

Hello guys, I want to test the short circuit current of Type3 and Type 4 Wind Generator or PV (WECC second generation models, i.e. the exciter is REECA1) by psse dynamic simulation and IEC60909. I want to use the EXAMPLE of psse but the IEC60909testnetworkwindPV.iec could not work well and there is no windpV.sav and .dyr.
Anyone here has good tools or ideas with psse short circuit current of WTG and PV simulution ? and how to use the IEC example of IEC60909testnetworkwind_PV.iec.

Thanks a lot!

edit retag flag offensive close merge delete

1 answer

Sort by ยป oldest newest most voted
1

answered 2018-10-17 10:39:55 -0500

jconto gravatar image

updated 2018-10-17 10:46:41 -0500

Simulation of the type 3, type 4 wind generator or PV short circuit current using psse dynamic simulation is just the same as testing a fault at the point-of-interconnection of the renewable plant. All inverter-based generation resources (type 3, type 4, PV plants) will limit the current output to just over 1 p.u. during faults (or short-circuits). Search the net for "model wind plants with PSSe" or "second generation of wind turbine models" Visit my google drive site and download rewind.zip and solarPVv33.zip, PSSe demo dynamic data set.

The short-circuit test under IEC60909 is done using the PSSe fault analysis tool with additional sequence network data (not a dynamic simulation.) Search the net for "PSSe IEC60909"

edit flag offensive delete link more

Your Answer

Please start posting anonymously - your entry will be published after you log in or create a new account.

Add Answer

[hide preview]

Question Tools

2 followers

Stats

Asked: 2018-10-16 22:31:26 -0500

Seen: 1,370 times

Last updated: Oct 17 '18