Simulation of the type 3, type 4 wind generator or PV short circuit current using psse dynamic simulation is just the same as testing a fault at the point-of-interconnection of the renewable plant. All inverter-based generation resources (type 3, type 4, PV plants) will limit the current output to just over 1 p.u. during faults (or short-circuits). Search the net for "model wind plants with PSSe" or "second generation of wind turbine models" Visit my google drive site and download rewind.zip and solarPVv33.zip, PSSe demo data set.

The short-circuit test under IEC60909 is done using the PSSe fault analysis tool with additional sequence network data (not a dynamic simulation.) Search the net for "PSSe IEC60909"

Simulation of the type 3, type 4 wind generator or PV short circuit current using psse dynamic simulation is just the same as testing a fault at the point-of-interconnection of the renewable plant. All inverter-based generation resources (type 3, type 4, PV plants) will limit the current output to just over 1 p.u. during faults (or short-circuits). Search the net for "model wind plants with PSSe" or "second generation of wind turbine models" Visit my google drive drive site and download rewind.zip and solarPVv33.zip, PSSe demo dynamic data set.

The short-circuit test under IEC60909 is done using the PSSe fault analysis tool with additional sequence network data (not a dynamic simulation.) Search the net for "PSSe IEC60909"