Ask Your Question
0

Fault Analysis in PSSE

asked 2018-06-11 00:31:59 -0500

kemalmals gravatar image

Hello. I have a project using PSSE. When I tried to do fault analysis I can't apply for L-G, L-L, and L-L-G. I only can apply the 3 phase fault. Is there any solution to solve this problem? Thank you

edit retag flag offensive close merge delete

1 answer

Sort by ยป oldest newest most voted
0

answered 2018-06-11 03:26:31 -0500

perolofl gravatar image

Sequence data (zero and negative) must be present in the save case in order to perform unbalanced faults.

edit flag offensive delete link more

Comments

@perolofl how to get sequence data from .raw file

Gloria.Z gravatar imageGloria.Z ( 2018-10-21 04:03:34 -0500 )edit

Raw-file only contains positive sequence data. Sequence data are in a .seq file.

perolofl gravatar imageperolofl ( 2018-10-21 06:12:24 -0500 )edit

Could you tell me how to get the sequence data? Thank you.

Gloria.Z gravatar imageGloria.Z ( 2018-10-21 09:06:16 -0500 )edit