0

Angle rotor in PSSE

My result simulation is performed with IEEE 24 bus and fault clearing time 1s. Rotor angle seem still Stable. I don't understand what's happenning. Hope anyone will help me... I use .sav and .dyr file in this https://drive.google.com/drive/folder... rotor angle: http://www.upsieutoc.com/image/cr8WUM
Thank you very much for your help

anonymous user
asked 2017-04-30 11:32:06 -0500, updated 2017-04-30 12:25:35 -0500
edit flag offensive 0 remove flag close merge delete

Comments

add a comment see more comments

3 Answers

0

Show the fault definition and the channels definition.

jconto's avatar
2.9k
jconto
answered 2017-05-01 22:07:35 -0500
edit flag offensive 0 remove flag delete link

Comments

add a comment see more comments
0

the fault: three 3 phase short circuit at line 14-16, after 1s it's cleared ,

channels: angle of generator at bus 1,16,21

melia4's avatar
26
melia4
answered 2017-05-01 22:29:01 -0500, updated 2017-05-01 22:29:20 -0500
edit flag offensive 0 remove flag delete link

Comments

add a comment see more comments
0

All machines are accelarating together during this fault and hence no machine is going out-of-step. It is more obvious to you if you plot all rotor angles!

perolofl's avatar
3.8k
perolofl
answered 2017-05-02 00:58:43 -0500
edit flag offensive 0 remove flag delete link

Comments

add a comment see more comments