Application of Unbalanced Faults in Positive Sequence Dynamic Simulation

My idea here is that, i will run a short-circuit analysis for the system under study using a different program and will get the single phase short circuit MVA values. I will compute for the pu impedance associated with the short circuit MVA value and apply it as a fault impedance in the PSSE dynamic simulation to emulate unbalanced disturbance.

May i know if someone here in the group did the same way? Otherwise, can you share your ways on modeling unbalanced faults in PSSE positive sequence dynamic simulation? Thanks.

anonymous user
asked 2017-05-24 09:12:17 -0500
edit flag offensive 0 remove flag close merge delete

Comments

add a comment see more comments

2 Answers

0

Thanks perolofl for this suggestion. I am familiar with this SCMU activity in PSS/E.

On your question, why use another progam to calculate unbalanced faults? It's because majority of the utilities prefer a short-circuit program other than PSS/E.

lmcqueen's avatar
76
lmcqueen
answered 2017-05-25 08:45:03 -0500
edit flag offensive 0 remove flag delete link

Comments

add a comment see more comments
0

Why use another program when you can do it directly in PSSE!

It is easy if sequence data are present in the saved case used for dynamic simulation. Then just select dynamic disturbance "Calculate and apply unbalanced bus fault". PSSE will automatically calculate the equivalent positive sequence fault admittance and insert it as fault admittance at the faulted bus.

If sequence data are not present in your dynamic saved case you can do a separate SCMU-calcĂșlation with a saved case containing the necessary sequence data (negative and zero sequence) and use the reported "POSITIVE SEQUENCE EQUIVALENT FAULT ADMITTANCE" as fault admittance in dynamic disturbance "Bus fault".

perolofl's avatar
3.8k
perolofl
answered 2017-05-25 03:20:31 -0500