How to incorporate LVRT in wind machines, PSS/E?

Both solar and wind. Is WT3G2 the right approach?

mdg194's avatar
1
mdg194
asked 2016-04-21 03:16:31 -0500
edit flag offensive 0 remove flag close merge delete

Comments

add a comment see more comments

2 Answers

0

Check the post "Under/Overvoltage relay" for information in using the model VTGTPAT to model a LVRT voltage profile, where each voltage 'point' is modeled with one relay. Same process for UV or OV relays (HVRT voltage profile).

jconto's avatar
2.9k
jconto
answered 2016-04-26 21:39:00 -0500
edit flag offensive 0 remove flag delete link

Comments

add a comment see more comments
0

short answer, yes. I suggest this page, it helped me alot:link text

tiagosantos's avatar
1
tiagosantos
answered 2016-04-26 11:43:25 -0500, updated 2016-04-26 11:44:04 -0500
edit flag offensive 0 remove flag delete link

Comments

Thanks for the response. Also, can LVRT be implemented with WT3G1? WT3G2 should be used alongside VTGTPAT right?

mdg194's avatar mdg194 (2016-04-27 04:40:13 -0500) edit

First just to clarify, the LHVRT (or VTGTPAT in psse) its optional for wt3g2. To implement a windturbine you must have a WT3G2, WT3E, WT3T and WT3P. The others models are optional. you can see more info here psspy.org/psse-help-forum/question/2659/how-to-incorporate-lvrt-in-wind-machines-psse/

tiagosantos's avatar tiagosantos (2016-04-28 10:32:05 -0500) edit