How to incorporate LVRT in wind machines, PSS/E?
Both solar and wind. Is WT3G2 the right approach?
First time here? We are a friendly community of Power Systems Engineers. Check out the FAQ!
Both solar and wind. Is WT3G2 the right approach?
Check the post "Under/Overvoltage relay" for information in using the model VTGTPAT to model a LVRT voltage profile, where each voltage 'point' is modeled with one relay. Same process for UV or OV relays (HVRT voltage profile).
short answer, yes. I suggest this page, it helped me alot:link text
First just to clarify, the LHVRT (or VTGTPAT in psse) its optional for wt3g2. To implement a windturbine you must have a WT3G2, WT3E, WT3T and WT3P. The others models are optional. you can see more info here psspy.org/psse-help-forum/question/2659/how-to-incorporate-lvrt-in-wind-machines-psse/