asked 2015-09-08 23:03:00 -0500

amir000888 gravatar image

i got this error "No type 3 (swing) bus in the network"..How to solve it???

edit retag flag offensive close merge delete

2 answers

Sort by ยป oldest newest most voted
1

answered 2015-09-08 23:22:55 -0500

tuton11 gravatar image

assign a generator bus as tupe 3 bus preferably the generator bus having highest generating capacity

edit flag offensive delete link more

Comments

Another criteria is to select the generator, among the largest, with the largest spin reserve (Pmax-Pgen). Once its type is changed to 3, solve a loadflow and check that it remains within limits in P and Q.

jconto gravatar imagejconto ( 2015-09-09 19:13:31 -0500 )edit
0

answered 2015-09-17 09:51:14 -0500

Nihal Mohan gravatar image

If you are doing a study involving DC lines, PSSE also requires to have a swing bus on the either side of a HVDC terminal.

edit flag offensive delete link more

Comments

Not true! Both terminals may be in the same AC-system. You need one swing bus in each separate AC-system.

perolofl gravatar imageperolofl ( 2016-09-20 13:18:15 -0500 )edit