psse error "No type 3 (swing) bus in the network"
i got this error "No type 3 (swing) bus in the network"..How to solve it???
First time here? We are a friendly community of Power Systems Engineers. Check out the FAQ!
i got this error "No type 3 (swing) bus in the network"..How to solve it???
assign a generator bus as tupe 3 bus preferably the generator bus having highest generating capacity
If you are doing a study involving DC lines, PSSE also requires to have a swing bus on the either side of a HVDC terminal.