psse error "No type 3 (swing) bus in the network"

i got this error "No type 3 (swing) bus in the network"..How to solve it???

amir000888's avatar
1
amir000888
asked 2015-09-08 23:03:00 -0500
edit flag offensive 0 remove flag close merge delete

Comments

add a comment see more comments

2 Answers

1

assign a generator bus as tupe 3 bus preferably the generator bus having highest generating capacity

tuton11's avatar
11
tuton11
answered 2015-09-08 23:22:55 -0500
edit flag offensive 0 remove flag delete link

Comments

Another criteria is to select the generator, among the largest, with the largest spin reserve (Pmax-Pgen). Once its type is changed to 3, solve a loadflow and check that it remains within limits in P and Q.

jconto's avatar jconto (2015-09-09 19:13:31 -0500) edit
add a comment see more comments
0

If you are doing a study involving DC lines, PSSE also requires to have a swing bus on the either side of a HVDC terminal.

Nihal Mohan's avatar
61
Nihal Mohan
answered 2015-09-17 09:51:14 -0500
edit flag offensive 0 remove flag delete link

Comments

Not true! Both terminals may be in the same AC-system. You need one swing bus in each separate AC-system.

perolofl's avatar perolofl (2016-09-20 13:18:15 -0500) edit