Ask Your Question
0

Why there are big osicilation in my PSS/E Photovoltaic (PV) project dynamic analysis?

asked 2015-04-25 18:01:00 -0600

Sam gravatar image

updated 2015-04-25 18:19:44 -0600

There is very big oscillation when connecting many PVs to the system and do the dynamic analysis. 1. All the PV generation I set control mode to +,-Q limits based on WPF. And I set the remote bus in dyr file as 0. 2. When no fault applied and more than two PVs are connected to the system, the suspect condition is OK, but the simulation output is not flat as output. 3. When I take all PV units and sub network out, the output is flat. The suspect conditions is OK. 4. When I only connect one PV to the system and do dynamic analysis, the output is flat and suspect conditions is OK. I hope someone can help me. Thank you!!

edit retag flag offensive close merge delete

Comments

Sam gravatar imageSam ( 2015-04-25 18:01:10 -0600 )edit

1 answer

Sort by » oldest newest most voted
0

answered 2015-04-26 15:41:09 -0600

jconto gravatar image

Some ideas: 1- Set all generation to control their own bus. 2- the swing generator (bus 1) was not a true 'infinite' machine. Better use a classical model, with no excitation model. 3- PV units have limited Pmax and Qmax, Qmin. I set 1.5 MW and +/- 0.5 Mvar. 4- Load needs to be converted before running a dynamic simulation.

JConto.

edit flag offensive delete link more

Your Answer

Please start posting anonymously - your entry will be published after you log in or create a new account.

Add Answer

[hide preview]

Question Tools

Stats

Asked: 2015-04-25 18:01:00 -0600

Seen: 1,958 times

Last updated: Apr 26 '15