How to model over frequency relay tripping?

asked 2026-03-18 14:52:38 -0500

updated 2026-03-24 17:56:32 -0500

I am trying to model relay trip action to trip loads/feeders for over-frequency conditions in PSSE dynamic simulations. However, I can't seem to find any suitable model. Most relays are based on underfrequency

LDSHBL, LDSHOW, LDSHZN, LDSHAR, LDSHAL

The only over-frequency relay I found are the:

FRQDCAT, and FRQTPAT,

However, they only disconnect generators, or the whole bus. Is their any over-frequency relay that would trip a load or a percentage of a load?

edit retag flag offensive close merge delete

1 answer

Sort by ยป oldest newest most voted
1

answered 2026-03-31 11:49:26 -0500

perolofl gravatar image

Do the following:

  1. Split the load bus and move the load to be tripped to the new bus (LBUS). Change the bus code to 2.
  2. Add a dummy generator at the load bus with Mbase=0.01, Qmax = Qmin = 0.
  3. Add dynamic model GENCLS to the dummy generator with H=0.001.
  4. Add dynamic model FRQDCAT with ICON(M)=LBUS, ICON(M+1)=LBUS and ICON(M+2)=generator id.

The load is now connected to a fictitious generator bus and model FRQDCAT can be used to trip the bus at overfrequency.

edit flag offensive delete link more

Comments

Thanks @perolofl

Mohamed_M gravatar imageMohamed_M ( 2026-03-31 15:58:14 -0500 )edit