0

Modelling SVC using Switched Shunt

Hello, I'm trying to model a SVC using "Switched Shunt" in both Steady State and Dynamic. The SVC is calculated to be +/- 100MVAR. Accordingly, I adjusted the parameters of Switched Shunt Data Record to be as follow: Bus Number : 202 Control Mode: (2) Continuous Cntrl Voltage Adjustment Method: Nearest Combination Vhi (pu) = 1.05 Vlo (pu) = 0.95 Block 1 steps = 1 , Block (1) Bstep (MVAR) = -100 Block 2 steps = 1 , Block (2) Bstep (MVAR) = 100

These settings work very good in load flow with base case & contingency conditions and in each case the SVC inject or absorb reactive power maintaining the voltage on busbar # 202 = 1 pu.

However, when I modeled the SVC in .dyr file with the following parameters: 202, 'CSSCST', 0, 3000.0, 0.00, 0.00, 2.4, 0.00, 0.00, 100.0, -100.0, 0.50 /

The dynamic does not initialize INITIAL CONDITIONS SUSPECT: I DSTATE(I) STATE(I) MODEL STATE BUS# X-- NAME --X BASKV ID 868 19.548 -10.444 CSSCST K 202 ZOZOCAIRE225 225.00

The -10.444 MVAR is the Initial MVAR (Base Case) in load flow solution.

PLEASE ADVISE WHAT COULD BE THE MISTAKE AND HOW CAN I SOLVE IT.

SamehKozman's avatar
41
SamehKozman
asked 2025-08-27 14:14:57 -0500
edit flag offensive 0 remove flag close merge delete

Comments

add a comment see more comments

1 Answer

0

Set Vhi = Vlo = 1.0 in load flow.

perolofl's avatar
3.8k
perolofl
answered 2025-08-28 00:48:21 -0500
edit flag offensive 0 remove flag delete link

Comments

Thank you for your answer. What will be the effect or why we have to do this?

SamehKozman's avatar SamehKozman (2025-08-28 05:17:21 -0500) edit

A continuous SVC should have a single voltage setpoint.

perolofl's avatar perolofl (2025-08-28 08:13:09 -0500) edit

Ok thank you so much. I modified it and also reduced the gain to only 5 and it initializes correctly. I have another question now if possible: Can I plot the MVAR output from this Switched Shunt (SVC) during dynamic simulation. HOW?

SamehKozman's avatar SamehKozman (2025-08-28 09:19:53 -0500) edit

The easiest solution is to split the bus and move the SVC to the new bus and add P&Q monitoring channels on the line (ZIL) between the buses.

perolofl's avatar perolofl (2025-08-28 14:40:29 -0500) edit

Words cannot adequately express my gratitude. I only have one step left.. psspy.branch_p_and_q_channel([202,1018,1]) python command will not make the PSSE plotting the P & Q So how can I solve for this? Also there is something strange .. the .out file is almost empty with less than 1KB!

SamehKozman's avatar SamehKozman (2025-08-28 17:10:45 -0500) edit