First time here? We are a friendly community of Power Systems Engineers. Check out the FAQ!

Ask Your Question
0

LTC Transformers on Reactive Power Study

asked Apr 2 '5

lmcqueen gravatar image

I'm performing reactive power study for a solar plant to determine compliance with FERC 827 and quantify if there is a need for additional reactive power compensation device.

I saw several studies where they consider LTC tap movement to increase reactive power capability at the POI but I'm wondering why it was done so because LTC movement is not even on the dynamic range. If somebody has some insights on this, I appreciate your comments.

1 answer

Sort by » oldest newest most voted
0

answered 3 hours ago

MarkG gravatar image

This is not so much a PSSPY question, but I will say that, at higher voltages, passive reactive devices (switched caps for example) will contribute more reactive power. A transformer LTC might be set to maximize capacitor voltage and thus get higher reactive performance. In many cases LTC tap position will be different for leading and lagging cases. For reactive capability validation, it is better to set transformer taps where aggregate plant reactive output meets criteria over the entire range of operating voltages. Apart from transformer taps, one must also consider allowable range at PV inverter terminals and collector equipment.

What did you mean by "LTC movement is not even on the dynamic range"?

link

Your Answer

Please start posting anonymously - your entry will be published after you log in or create a new account.
Want to format code in your answer? Here is a one minute demo on Youtube

Add Answer

[hide preview]

Question Tools

1 follower

Stats

Asked: Apr 2 '5

Seen: 31 times

Last updated: 4 hours ago