machine modeling in steady state for solar inverter

In PSSE, while modeling solar inverter as a machine for steady state. How do you define the parameters like X source , Subtransient,Transient,Synchronius, Zero and Negative impedance while modeling ? What values to be considered ? Thanks in Advance

Vikas07's avatar
1
Vikas07
asked 2020-10-10 03:50:51 -0500
edit flag offensive 0 remove flag close merge delete

Comments

add a comment see more comments

2 Answers

0

Based the fault current contribution from Inverter (typically 1.1 times the inverter rated current), the Impedance can be calculated and parameters like X source , Sub transient, Transient, Synchronous reactance shall be kept Identical in this case.

Berwin's avatar
113
Berwin
answered 2020-10-10 05:39:21 -0500
edit flag offensive 0 remove flag delete link

Comments

Thanks for the reply. I know the maximum converter current limit of the inverter. Eg. 1.068 pu. Can i define all the impedance parameters as 1/1.068 = 0.9363 pu ?

Vikas07's avatar Vikas07 (2020-10-10 07:58:42 -0500) edit

Yes, exactly. You can use the same parameters for PV inverter in the steady state model.

Berwin's avatar Berwin (2020-10-11 03:03:15 -0500) edit
add a comment see more comments
0

Xsource is usually set at a very large value e.g. 9999 p.u. However, please note that manufacturer's data of inverter shall be consulted before doing the modeling work. They typically provide modeling procedure of inverter for PSS/E steady-state and dynamic studies. An Aspen Oneliner modeling note is also given for short-circuit studies as well.