IEEE39 - inertia of generators
hello Jconto sir, i used your IEEE39 drive files. but why the inertia of all generators are same? can we change as nearer to that like increase or decrease?
First time here? We are a friendly community of Power Systems Engineers. Check out the FAQ!
hello Jconto sir, i used your IEEE39 drive files. but why the inertia of all generators are same? can we change as nearer to that like increase or decrease?
There is no dynamic data for the original IEEE39 data set. The same inertia value for all generators is a by-product of lazy copy/paste from my part. The final data set behaves well dynamically, but you can change those inertia values (or other dyre parameters) to more realistic ones according to the size and type of the machines.
Asked: 2025-03-31 08:32:44 -0500
Seen: 889 times
Last updated: Mar 31 '25