IEEE39 - inertia of generators

asked 2025-03-31 08:32:44 -0600

swap gravatar image

updated 2025-03-31 17:46:48 -0600

jconto gravatar image

hello Jconto sir, i used your IEEE39 drive files. but why the inertia of all generators are same? can we change as nearer to that like increase or decrease?

edit retag flag offensive close merge delete

1 answer

Sort by ยป oldest newest most voted
0

answered 2025-03-31 17:44:28 -0600

jconto gravatar image

There is no dynamic data for the original IEEE39 data set. The same inertia value for all generators is a by-product of lazy copy/paste from my part. The final data set behaves well dynamically, but you can change those inertia values (or other dyre parameters) to more realistic ones according to the size and type of the machines.