IEEE39 - inertia of generators

hello Jconto sir, i used your IEEE39 drive files. but why the inertia of all generators are same? can we change as nearer to that like increase or decrease?

swap's avatar
1
swap
asked 2025-03-31 08:32:44 -0500
jconto's avatar
2.9k
jconto
updated 2025-03-31 17:46:48 -0500
edit flag offensive 0 remove flag close merge delete

Comments

add a comment see more comments

1 Answer

0

There is no dynamic data for the original IEEE39 data set. The same inertia value for all generators is a by-product of lazy copy/paste from my part. The final data set behaves well dynamically, but you can change those inertia values (or other dyre parameters) to more realistic ones according to the size and type of the machines.