run dynamic simulation for Ieee39-bus

hello everyone I'm still have some mistake in dynamic simulation for IEEE-39bus after any disturbance (ex. loss of Generator or trip line..) More clearly it's shown in the output results : frequency and voltage "NAN" I do not know what's the wrong I selected channel setup wizard categories to output : Bus
please I need help and thank you all

Yasmine's avatar
5
Yasmine
asked 2015-08-23 20:07:33 -0500
edit flag offensive 0 remove flag close merge delete

Comments

add a comment see more comments

1 Answer

0

Hi Yasmine,

Normally the NaN value occurs when the simulation doesn't converge correctly. In my experience I've gotten NaN values when the channel values blow up. The first thing to check is that the initial solution is flat start before any contingencies occur. There is a possibility that the particular contingency you create is causing the solution to blow up as your case cannot handle it, or it can have something to do with the actual dynamics of the generators you specified in your .dyr file.

Lassettc's avatar
17
Lassettc
answered 2015-09-08 15:56:46 -0500
edit flag offensive 0 remove flag delete link

Comments

add a comment see more comments