Dear Experts, Can you guide me in modeling 5 5winding transformer in PSS/E both in steady state and dynamics? Regards, Chandv

edit retag flag offensive close merge delete

Comments

Can you specify what is connected to the five winding and the complete data from the short circuit test?

perolofl gravatar imageperolofl ( 2024-11-30 11:47:39 -0500 )edit

1 answer

Sort by ยป oldest newest most voted
0

answered 2024-11-30 20:56:55 -0500

chandv gravatar image

I am unable to upload image here. It is 4 LV (0.66 KV) and 1 HV (33KV) transformer. LV side is connected to either solar inverter or BESS PCS. 33 KV Side will be connected to HT panel. In India 5 winding transformers in solar and BESS are used. However, PSS/E only has 2 wdg and 3 wdg transformers. It is possible to model using multiple of 2 or 3 wdg transformers. But in that case, will the final results will be impacted or what can be better modeling practice? In multiple transformer model, splitting of impedance is important, which is generally not specified in datasheet. Insite in 5 wdg transformer modeling will be much helpful. Thank you in advance.