TwoWindingTransformer parameters into CIM

Hi,

I am working with CIM files generated with ODMS. If anybody has experience with that, my question is regarding specific parameters from PSSE that belong the the transformer model. They belong to the pti rdf schema, which are not standard within the CIM

<pti:PowerTransformer.rma>
<pti:PowerTransformer.rmi>
<pti:PowerTransformer.nmetr>

Anybody knows what are these parameters? I cannot see any documentation related to them ( and... I cannot check within the PSSE because my license just expired :P )

Thank you!!

fran_jo's avatar
37
fran_jo
asked 2018-02-15 13:12:54 -0500
edit flag offensive 0 remove flag close merge delete

Comments

add a comment see more comments

1 Answer

1

I know nothing about CIM data but it seems to be maximum ratio, minimum ratio and the bus number of the metered end.

perolofl's avatar
3.8k
perolofl
answered 2018-02-15 14:59:23 -0500
edit flag offensive 0 remove flag delete link

Comments

Thanks @perolofl! Sounds reasonable!

fran_jo's avatar fran_jo (2018-02-15 17:35:13 -0500) edit
add a comment see more comments