0

How to get three-winding transformer power flow

Hi everybody! , I’m trying to get the power flow in a three-winding transformer. I tried function TR3DT2 but it seems to be only for impedance. BRNFLO doesn´t work and I found no other function to get the power flow. Should I make a python script? Thanks a lot in advance!

SAE_2016's avatar
13
SAE_2016
asked 2017-07-25 10:59:14 -0500, updated 2017-07-25 11:00:01 -0500
edit flag offensive 0 remove flag close merge delete

Comments

add a comment see more comments

2 Answers

0

YES! wnddt2 is the right function. Thank you very much for your quick answer

SAE_2016's avatar
13
SAE_2016
answered 2017-07-25 14:47:56 -0500
edit flag offensive 0 remove flag delete link

Comments

add a comment see more comments
0

Have you considered WNDDAT. It can return percent current or MVA loading of 3 winding transformer.

nelak's avatar
1
nelak
answered 2017-07-25 12:57:39 -0500
edit flag offensive 0 remove flag delete link

Comments

add a comment see more comments

Your Answer

Login/Signup to Answer