Power flow mismatch calculation fdns

Hi, I have a question about power flow mismatch calculation in psspy when I use this code psspy.fdns and the IERR = 4 "buses in island(s) without a swing bus; use activity TREE". I am using the following code for power flow mismatch calculation. It is wondering that when the IERR = 4, I also get some value for mva however I don't know what this value is and how it is calculated! I appreciate your sharing your experience with this issue.

psspy.fdns([0,0,0,1,1,0,99,0]) mva = psspy.sysmsm()

anonymous user
asked 2023-02-19 13:38:36 -0500
edit flag offensive 0 remove flag close merge delete

Comments

add a comment see more comments

2 Answers

0

The system mismatch is calculated from the actual values of bus voltages (magnitude and angle).

The solution with FDNS is aborted since there is at least one island in the network.

perolofl's avatar
3.8k
perolofl
answered 2023-02-20 03:08:45 -0500
edit flag offensive 0 remove flag delete link

Comments

add a comment see more comments
0

The mismatch value from sysmsm should be approximately less than 10. For a small network, the value is often less than 1. For a large network (thousands of buses) up to 5 might be common. If you get a value in the thousands or greater, the loadflow solution is very bad. To me, it is very good practice to consider the system mismatch to check that the results are valid.

If you are getting the message to run TREE, then you need to run TREE to switch off the isolated buses before running a load flow.