1

Make Optimal Power Flow solutions more realistic

  • retag add tags

Does anyone have any tips that would help make optimal power flow produce more realistic flows and loading? How do you do a sanity check on your optimal power flow solution?

jtrain's avatar
411
jtrain
asked 2012-02-04 04:28:44 -0500
edit flag offensive 0 remove flag close merge delete

Comments

add a comment see more comments

1 Answer

1

Here's my experience with OPF in PSS/E.

I was optimizing the shunt capacitor size and location. In OPF, I defined the candidate buses with base case plus contingencies. When OPF provided the shunt compensation location and size, I simulated the case with the shunt capacitor in place and applied the contingencies, if any, and see if the voltages would be at acceptable magnitudes per criteria.

This is a good check if the OPF "really" gave the optimal capacitor size and location.

EBC's avatar
151
EBC
answered 2012-10-10 20:28:47 -0500
edit flag offensive 0 remove flag delete link

Comments

@EBC can you give us a peep at your code?

amaity's avatar amaity (2012-10-11 20:50:33 -0500) edit

amaity, I don't have a python code on this strategy...I'm sorry...usually I have an idev or python recorded but I don't have those now when I resigned from PTI...thanks.

EBC's avatar EBC (2012-10-23 16:14:42 -0500) edit

If i dont want to use any python routine then what would be the strategy to find optiml power flow n PSSE. When I solve myt case withOPF,the solution case was blown up.

USMAN KHALID's avatar USMAN KHALID (2013-07-11 23:40:26 -0500) edit

@EBC how OPF provide the optimal size and location for compensation? there is a special code for this?

yaya's avatar yaya (2017-05-18 05:11:14 -0500) edit
add a comment see more comments