Why do it get current in other phases when i short circuit one phase (Single line to ground fault). IEC 60909 calculations

asked 2023-01-04 23:32:53 -0600

CynicalSuka gravatar image

All loads set to zero. All shunts set to zero. I get current in other phases when i short circuit one phase only meaning single line to ground phase. By theory current should only flow in faulted phase as all the loads are open circuited, all shunts are ignored in all sequences etc

edit retag flag offensive close merge delete

1 answer

Sort by » oldest newest most voted
0

answered 2023-01-10 12:05:04 -0600

perolofl gravatar image

updated 2023-01-13 07:53:30 -0600

In a network there will be currents flowing in the healthy phases at LG-faults, even if all loads and shunts are ignored.

At LG-fault the sequence currents are equal at the fault location, but the impedance and layout of the positive, negative and zero sequence systems are different.

So, normally there are currents in the healthy phases of the lines/transformers feeding the faulted bus.

EDIT: An example with a simple non-loaded system with only reactances as shown below:

image description

The Thevenin positive sequence reactance at bus 3 is 0.45 pu and the zero sequence reactance is 0.08 pu. The zero sequence reactance for the branches is 0.6 pu each, and the zero sequence reactance of each grounded transformer is 0.1 pu.

LG-fault at bus 3 gives the following results with ASCC:

AT BUS      3     [C           400.00] AREA    1  *** FAULTED BUS IS:      3     [C           400.00] ***   0 LEVELS AWAY ***
 PRE  FAULT (kV L-G)  VA:/230.94/30.00
 POST FAULT (kV L-G)  V+:/124.90/30.00  V-:/106.04/-150.00  V0:/18.85/-150.00  VA:/0.00/0.00  VB:/201.99/-68.05  VC:/201.99/128.05
 THEVENIN IMPEDANCE, X/R  (PU)  Z+:0.000000+j0.450000, 9999.999  Z-:0.000000+j0.450000, 9999.999  Z0:0.000000+j0.080000, 9999.999
                                                  X------------------------------------LINE TO GROUND (LG) FAULT-----------------------------------X
 X----------- FROM ------------X AREA CKT I/Z         /I+/   AN(I+)     /I-/   AN(I-)     /I0/   AN(I0)    /3I0/   AN(I0)   RE(Z0)   IM(Z0)  APP X/R
      2     [B           400.00]    1 1   AMP/PU      73.6   -60.00     73.6   -60.00     14.7   -60.00     44.2   -60.00 0.000000-0.200000 9999.999
      2     [B           400.00]    1 2   AMP/PU      73.6   -60.00     73.6   -60.00     14.7   -60.00     44.2   -60.00 0.000000-0.200000 9999.999
      4     [D           135.00]    1 1   AMP/PU       0.0     0.00      0.0     0.00    117.8   -60.00    353.5   -60.00 0.000000 0.000000  0.00000
 INITIAL SYM. S.C. CURRENT(I''k)(RMS)     AMP        147.3   -60.00    147.3   -60.00    147.3   -60.00    441.8   -60.00
                                                  --------------------------------------------------------------------------------------------------
 X----------- FROM ------------X AREA CKT I/Z         /IA/   AN(IA)     /IB/   AN(IB)     /IC/   AN(IC)                     RE(ZA)   IM(ZA)  APP X/R
      2     [B           400.00]    1 1   AMP/PU     162.0   -60.00     58.9   120.00     58.9   120.00                   -0.00000 0.236364 9999.999
      2     [B           400.00]    1 2   AMP/PU     162.0   -60.00     58.9   120.00     58.9   120.00                   -0.00000 0.236364 9999.999
      4     [D           135.00]    1 1   AMP/PU     117.8   -60.00    117.8   -60.00    117.8   -60.00                   -0.01540 0.108889  7.07254
 INITIAL SYM. S.C. CURRENT(I''k)(RMS)     AMP        441.8   -60.00      0.0     0.00      0.0     0.00
 ---------------------------------------------------------------------------------------------------------------------------------------------------

There is only fault current in phase A at bus 3 (441 ... (more)

edit flag offensive delete link more

Comments

Why do i get current in B and C phase if only A phase is grounded. By theory current in B and C phase should be zero if all loads and shunts are ignored.

CynicalSuka gravatar imageCynicalSuka ( 2023-01-12 10:39:26 -0600 )edit

See my updated answer!

perolofl gravatar imageperolofl ( 2023-01-13 04:31:48 -0600 )edit

i think you may have missed some important things in your example. Transformer connection codes and phase shift! According to theory there should be current in only A and C phase coming from Bus 4. PSSE PAG Vol 1 has a nice section dedicated to wrong SC calculations if phase shift is ignored.

CynicalSuka gravatar imageCynicalSuka ( 2023-01-13 10:57:46 -0600 )edit

11.2.5.2 Effect of Neglecting Transformer Phase Shift <-----section of PSSE PAG Vol 1

CynicalSuka gravatar imageCynicalSuka ( 2023-01-13 10:59:02 -0600 )edit

still not convinced! In unloaded system no current should flow in other phases. Only Delta-star transformer can make the fault current on one phase of star side to flow in two phases on delta side. thats the theory

CynicalSuka gravatar imageCynicalSuka ( 2023-01-13 11:33:34 -0600 )edit

There is nothing missed in my example. Please take you time and model the same system yourself, and you will understand that the results are correct. You have misunderstood the theory.

perolofl gravatar imageperolofl ( 2023-01-14 08:39:50 -0600 )edit

The transformer phase shift will only affect currents at the other side of the transformer. I.e., the currents at bus 4. Here there are no current at bus 4 (no generator and grounded wye-winding at bus 3.

perolofl gravatar imageperolofl ( 2023-01-14 08:42:35 -0600 )edit

A nooby question. Why are currents flowing from bus 4 which is essentially a floating bus?

CynicalSuka gravatar imageCynicalSuka ( 2024-08-24 12:20:17 -0600 )edit

What do you mean? There is no current flowing from bus 4.

perolofl gravatar imageperolofl ( 2024-08-24 23:28:22 -0600 )edit

X----------- FROM ------------X AREA CKT I/Z /IA/ AN(IA) /IB/ AN(IB) /IC/ AN(IC) RE(ZA) IM(ZA) APP X/R 4 [D 135.00] 1 1 AMP/PU 117.8 -60.00 117.8 -60.00 117.8 -60.00 -0.01540 0.108889 7.07254

CynicalSuka gravatar imageCynicalSuka ( 2024-08-31 06:39:44 -0600 )edit

117 ampere current in all ABC phases with phase angle of -60 flowing from bus 4

CynicalSuka gravatar imageCynicalSuka ( 2024-08-31 06:41:26 -0600 )edit

It´s the zero sequence current flowing into the grounded Y-winding. Please read about symmetrical components and zero sequence for grounded WhyDelta transformers. The current is flowing in the 400 kV winding. There is no current in the 135 kV winding, i.e. no current flowing from bus 4!!!

perolofl gravatar imageperolofl ( 2024-08-31 09:00:45 -0600 )edit

I know results shows I0=117.8A but why does results under IA, IB, IC showing 117.8 A from bus 4? Maybe i am reading it wrong. Maybe from bus column means current coming from the direction of bus 4 towards bus 3 not necessarily from bus 4 itself. It makes sense then. Currents coming from Y side.

CynicalSuka gravatar imageCynicalSuka ( 2024-09-01 00:01:44 -0600 )edit

The Table shows the results at the faulted bus, bus number 3!!!! Of course the meaning is ""From the object connected to bus 4". In this case the WhyDelta transformer.

perolofl gravatar imageperolofl ( 2024-09-01 01:25:11 -0600 )edit