Change generator output during dynamic simulation

asked 2022-10-27 15:29:05 -0600

Erandika gravatar image

updated 2022-10-27 15:38:34 -0600

Hi,

Is there any method to change the generator power output during a dynamic simulation?

For ex: Pout initial = 600 MW, Pout after disturbance = 400 MW

I tried CHANGE_GREF function and INCREMENT_GREF functions. But I do not see any change happened for the power output in the plots.

edit retag flag offensive close merge delete

Comments

I assume you have a governor model connected to the generator!?

perolofl gravatar imageperolofl ( 2022-10-27 15:47:54 -0600 )edit

Yes, WSIEG1 model

Erandika gravatar imageErandika ( 2022-10-27 15:49:26 -0600 )edit

Can you show the data for the model?

perolofl gravatar imageperolofl ( 2022-10-28 13:39:02 -0600 )edit

1 answer

Sort by ยป oldest newest most voted
0

answered 2022-10-28 22:06:12 -0600

Tassie Dave gravatar image

Change_gref looks like it should work. You could check the associated VAR L+0="referece" to see if it has been changed by your command. And maybe look at the other VARs while you are at it; the change should ripple through the controller to its output. Dave Hodson, Dynamica