Change generator output during dynamic simulation

asked Oct 27 '2

Erandika gravatar image

updated Oct 27 '2

Hi,

Is there any method to change the generator power output during a dynamic simulation?

For ex: Pout initial = 600 MW, Pout after disturbance = 400 MW

I tried CHANGE_GREF function and INCREMENT_GREF functions. But I do not see any change happened for the power output in the plots.

Comments

I assume you have a governor model connected to the generator!?

perolofl gravatar imageperolofl (Oct 27 '2)

Yes, WSIEG1 model

Erandika gravatar imageErandika (Oct 27 '2)

Can you show the data for the model?

perolofl gravatar imageperolofl (Oct 28 '2)

1 answer

Sort by » oldest newest most voted
0

answered Oct 29 '2

Tassie Dave gravatar image

Change_gref looks like it should work. You could check the associated VAR L+0="referece" to see if it has been changed by your command. And maybe look at the other VARs while you are at it; the change should ripple through the controller to its output. Dave Hodson, Dynamica