asked 2013-05-10 08:34:27 -0500

ruk gravatar image

Hi! In PSSE, how should I use CONL to convert my constant P-Q loads to constant impedance loads?

edit retag flag offensive close merge delete

2 answers

Sort by » oldest newest most voted
1

answered 2013-05-17 19:27:25 -0500

yfwing gravatar image

What types of load you should use totally depend on the actual characteristics of the loads. For example, you may want to use constant impedance type for heating loads (active power). If you don't know the real characteristics of the loads, you can try to use 100% constant impedance (P), and 100% constant current (Q) or you can refer to the standards in your system planning area (such as WECC).

edit flag offensive delete link more
0

answered 2013-05-21 05:19:57 -0500

Amir gravatar image

I am working on Single line diagram(SLD) development using python.And i need to know know the locations of buses. ANYONE can tell me the Command to extract "bus laocation" from the .sav file. REGARDS..!!

edit flag offensive delete link more

Comments

For future seekers: Use abusint command. ierr, buses = psspy.abusint(-1, string = "NUMBER")

Aryan Ritwajeet Jha gravatar imageAryan Ritwajeet Jha ( 2021-11-27 17:08:30 -0500 )edit