impedance load

Hi! In PSSE, how should I use CONL to convert my constant P-Q loads to constant impedance loads?

ruk's avatar
41
ruk
asked 2013-05-10 08:34:27 -0500
edit flag offensive 0 remove flag close merge delete

Comments

add a comment see more comments

2 Answers

1

What types of load you should use totally depend on the actual characteristics of the loads. For example, you may want to use constant impedance type for heating loads (active power). If you don't know the real characteristics of the loads, you can try to use 100% constant impedance (P), and 100% constant current (Q) or you can refer to the standards in your system planning area (such as WECC).

yfwing's avatar
436
yfwing
answered 2013-05-17 19:27:25 -0500
edit flag offensive 0 remove flag delete link

Comments

add a comment see more comments
0

I am working on Single line diagram(SLD) development using python.And i need to know know the locations of buses. ANYONE can tell me the Command to extract "bus laocation" from the .sav file. REGARDS..!!

Amir's avatar
21
Amir
answered 2013-05-21 05:19:57 -0500
edit flag offensive 0 remove flag delete link

Comments

For future seekers: Use abusint command. ierr, buses = psspy.abusint(-1, string = "NUMBER")