Ask Your Question
0

some questions about power flow adjustment

asked 2022-03-22 09:14:34 -0600

greatly gravatar image

updated 2022-03-22 09:15:18 -0600

Hello everyone

I want to carry out some experiments of power flow adjustment in PSS/E. 1)When I set the system power imbalance, the power flow solver can always make the system converge. However, in some cases, the power of the balancing machine will exceed the limit. I know that if the power of the balancing machine does not exceed the limit, the power flow of the system will not converge. However, I need this sick power flow scenario, because I hope to change this situation by switching capacitors /reactors. How can I avoid the balancing machine power out of limit by setting PSS/E. 2)Since I have not used capacitors/reactors in PSS/E before, I do not know the meaning of some of these parameters. For example, I don't know how to choose the control model and adjustment method. I don't know the meaning of binit, BLK Steps and BLK Bstep (Mvar).

I really need your help. Any idea or suggestion is OK. I would be very grateful, and I look forward to sharing these issues with you.

edit retag flag offensive close merge delete

Comments

What do you mean with balancing machine? Swing bus?

perolofl gravatar imageperolofl ( 2022-03-23 09:08:15 -0600 )edit

1 answer

Sort by » oldest newest most voted
0

answered 2022-03-23 09:07:35 -0600

perolofl gravatar image

Read about switched shunts in the manual! If you still don't understand how to use them, then you can use fixed shunts instead. They are straight forward to implement.

edit flag offensive delete link more

Comments

Thank you very much. It is very useful.

greatly gravatar imagegreatly ( 2022-03-23 10:12:19 -0600 )edit

Your Answer

Please start posting anonymously - your entry will be published after you log in or create a new account.

Add Answer

[hide preview]

Question Tools

1 follower

Stats

Asked: 2022-03-22 09:14:34 -0600

Seen: 558 times

Last updated: Mar 23 '22