What would be PV analysis termination criteria?

Regarding PV analysis in PSSe, what is the termination criteria if we uncheck the voltage limit?

I run a PV analysis without voltage limit and chose 0.5 MW as mismatch tolerance. Is the mismatch tolerance considered as termination for increasing the power transfer to the next step?

if so, It doesn't indicate the divergence in power flow computation and only considers the mismatch for the next level. Am I right?

For example, what would be the termination condition here ( there is no low voltage limit check, and mismatch tol. is 0.5 MW)?

MW TRANSFER-> 0.000 100.000 200.000 300.000 400.000

LARGEST MVA MISMATCH 0.01791 0.06002 0.06557 0.16307 0.45200

TOTAL MVA MISMATCH 0.02811 0.12424 0.13641 0.35181 1.12765

CONVERGED YES YES YES YES YES

CONVERGE CONDITION

Also, what is the meaning of 'CONVERGE CONDITION' here which they all are empty here?!

Thanks a lot for supporting me here!

Moji

Moji's avatar
1
Moji
asked 2022-03-09 17:58:36 -0500
edit flag offensive 0 remove flag close merge delete

Comments

add a comment see more comments

1 Answer

0

Check the post "How does contingency analysis can iterate over a defined vector of line flow changes?" for some answers. Usually terminating criteria are transfer that do not converged or that reach its transfer limit. In your transfer example above, set the max transfer between regions to a large number, like 10000

jconto's avatar
2.9k
jconto
answered 2022-03-10 17:48:21 -0500