Reactive power control

asked 2021-12-16 09:12:59 -0500

Cris_Mx gravatar image

I have a system with a generator conected to transformer and this connected to a swing bus and when I apply a voltage step of 2%, I want the reactive power to go from -12 Mvar to 8 Mvar. But it only increases from -12 Mvar to -3 Mvar.

edit retag flag offensive close merge delete

Comments

Generators control voltage. They will put out whatever Mvar is needed to control a voltage. Sounds like you want to control Mvar and voltage independently, but they are dependent on eachother..

likethevegetable gravatar imagelikethevegetable ( 2021-12-17 18:37:24 -0500 )edit

2 answers

Sort by ยป oldest newest most voted
0

answered 2021-12-20 07:50:30 -0500

ffl gravatar image

A couple of questions: 1. Did you use a PLBVFU1 model at the system slack to perform the voltage step test? 2. Was your generator connected to an excitation system?

When I perform step response tests, I use PLBVFU1 model for the system slack bus and provide step input playback signals (e.g., voltage and frequency). I will let the generator and plant control models respond and from there do the necessary parameter adjustments in order to obtain the desired response and output levels.

edit flag offensive delete link more
0

answered 2021-12-17 02:02:41 -0500

perolofl gravatar image

You are applying a 2% voltage change and get 9 Mvar change, but you want to get 20 Mvar change instead!? If so, you have to change the transformer reactance with the factor 9/20, i.e. multiply the reactance with 0.45.