SVC and Induction Motors in the same bus

asked Jun 23 '1

KM gravatar image

Can we install a SVC in a bus where we have induction motors as loads? This affects bus type (SVC will be switched off unless the load bus becomes a gen bus. Any idea on how to model this in PSSE. Thanks.

1 answer

Sort by » oldest newest most voted
0

answered Jun 23 '1

perolofl gravatar image

You can have an SVC modelled as a generator and induction motors as loads at the same bus. The bus type must be 2. It is ok to have loads at generator buses.

link

Comments

Thank you. Appreciated

KM gravatar imageKM (Jun 23 '1)