Ask Your Question
0

SVC and Induction Motors in the same bus

asked 2021-06-22 23:35:24 -0600

KM gravatar image

Can we install a SVC in a bus where we have induction motors as loads? This affects bus type (SVC will be switched off unless the load bus becomes a gen bus. Any idea on how to model this in PSSE. Thanks.

edit retag flag offensive close merge delete

1 answer

Sort by ยป oldest newest most voted
0

answered 2021-06-23 03:23:47 -0600

perolofl gravatar image

You can have an SVC modelled as a generator and induction motors as loads at the same bus. The bus type must be 2. It is ok to have loads at generator buses.

edit flag offensive delete link more

Comments

Thank you. Appreciated

KM gravatar imageKM ( 2021-06-23 05:46:38 -0600 )edit

Your Answer

Please start posting anonymously - your entry will be published after you log in or create a new account.

Add Answer

[hide preview]

Question Tools

1 follower

Stats

Asked: 2021-06-22 23:35:24 -0600

Seen: 276 times

Last updated: Jun 23 '21