how we make the choice of swing bus ?
When choosing the swing bus do we make the choice based on the machine that produces the biggest Pgen in the network or the machine with the highest value of inertia constant H ? Please help thnx in advance.
First time here? We are a friendly community of Power Systems Engineers. Check out the FAQ!
When choosing the swing bus do we make the choice based on the machine that produces the biggest Pgen in the network or the machine with the highest value of inertia constant H ? Please help thnx in advance.
The inertia constant has no effect in load flow calculation.
Normally you select a large generator as swing bus. However, any bus can be selected as swing, there is no need for a generator at the swing bus.
The most important is that the swing bus is electrically strong and is able to absorb any active power imbalance created when tripping generators, loads, HVDC lines, etc or after scaling total load/generation in the whole network or a subsystem.
A swing bus at high voltage level (e.g. 400 or 500 kV) is stronger than a swing bus at generator level (15-25 kV).
When performing voltage stability studies it is also good to locate the swing bus outside of the studied area, since the swing bus has no reactive power limits.
Asked: May 31 '1
Seen: 1,238 times
Last updated: Jun 03 '21
Is there any way to convert a .sav to .xlxs using psspy?
How to use PSS@E Renewable Model Packages .exe file in PSSE? Thank you
psspy can't run with another case without any exception
Split a system in to two networks
Capture keyboard interrupt in PSS/E script?
How to assing an item to a draw in the diagram
Can Electric Vehicle be modelled in PSSE ?
Why there are big osicilation in my PSS/E Photovoltaic (PV) project dynamic analysis?