How to simulate higher voltage
What is the best way to increase the voltage in the entire network to the limit values?
First time here? We are a friendly community of Power Systems Engineers. Check out the FAQ!
What is the best way to increase the voltage in the entire network to the limit values?
It would be good to know why you want an entire network in a high voltage state.
You can decrease the reactive consumption from loads (not a realistic scenario) or raised reactive injection (turn on capacitors or set generator voltage setting point to higher values).
Remember that voltage has a local impact so if you want to test a 'device' under high voltage condition, a localize high voltage condition can be created nearby such device instead of system wide HV conditions.
Asked: 2021-04-24 08:48:25 -0500
Seen: 181 times
Last updated: Apr 26 '21
HOW TO CALCULATE FVSI FROM DYNAMIC SIMULATION
Relative Voltage Angle for Dynamics
Unbalanced fault (slg) in dynamic simulation
Stability analysis for PV and Wind
Power flow results of SMIB in PSS/E do not match the hand calculations
Cut and paste Networks by Voltage Level