0

CHSB Monitor Machine Apparent Impedance

psspy.chsb can monitor apparent impedance by setting STATUS(5)=22. Did anyone know how this apparent impedance being calculated during time domain simulation. Moreover, is there any difference between calculating apparent impedance for wind generator and synchronous generator. Thanks !

wayne850306's avatar
1
wayne850306
asked 2021-01-27 15:24:20 -0500
edit flag offensive 0 remove flag close merge delete

Comments

add a comment see more comments

1 Answer

1

The apparent impedance is calculated from the apparent power S (P + jQ) and the voltage at the generator terminal (U**2/S).

perolofl's avatar
3.8k
perolofl
answered 2021-01-28 10:40:15 -0500