Question on PSSE terminology
Can someone explain the term ZSORCE, XTRAN, GENTAP please?
First time here? We are a friendly community of Power Systems Engineers. Check out the FAQ!
For a synchronous generator XSORCE is the subtransient reactance, Xd”.
XTRAN and GENTAP are only used if the step-up transformer is not modelled in load flow, i.e. the generator is connected directly at the high tension side.
Thank you. Do you mean XTRAN and GENTAP are only used if the step-up transformer is modeled in load flow? Above you said is not
No, I mean what I wrote. You can ignore XTRAN and GENTAP if the step-up transformer is modelled in the saved case. If so, the transformer is already modelled and there is no need to enter the data in the machine record.