Ask Your Question
0

Question on PSSE terminology

asked 2020-07-30 15:45:23 -0600

Jbaker gravatar image

Can someone explain the term ZSORCE, XTRAN, GENTAP please?

edit retag flag offensive close merge delete

3 answers

Sort by » oldest newest most voted
0

answered 2020-07-31 03:07:29 -0600

perolofl gravatar image

For a synchronous generator XSORCE is the subtransient reactance, Xd”.

XTRAN and GENTAP are only used if the step-up transformer is not modelled in load flow, i.e. the generator is connected directly at the high tension side.

edit flag offensive delete link more

Comments

Thank you. Do you mean XTRAN and GENTAP are only used if the step-up transformer is modeled in load flow? Above you said is not

Jbaker gravatar imageJbaker ( 2020-08-04 13:17:06 -0600 )edit

No, I mean what I wrote. You can ignore XTRAN and GENTAP if the step-up transformer is modelled in the saved case. If so, the transformer is already modelled and there is no need to enter the data in the machine record.

perolofl gravatar imageperolofl ( 2020-08-07 04:17:49 -0600 )edit
0

answered 2020-08-05 04:44:34 -0600

lmcqueen gravatar image

Using XTRAN and GENTAP means you are modeling the generator step-up transformer implicitly (i.e. unit-connected). See the Program Operation Manual for more information.

edit flag offensive delete link more
0

answered 2020-07-30 18:17:39 -0600

JbFord gravatar image

p.u Generator Dynamic Impedance, ZSORCE p.u. impedance XTRAN = RT, XT on machine MVA base p.u. off-nominal turns ratio (GENTAP) entered in the machine impedance

edit flag offensive delete link more

Comments

Thank you. XTRAN and GENTAP are only used if the step-up transformer is modeled in load flow, correct?

Jbaker gravatar imageJbaker ( 2020-08-04 13:17:50 -0600 )edit

Your Answer

Please start posting anonymously - your entry will be published after you log in or create a new account.

Add Answer

[hide preview]

Question Tools

1 follower

Stats

Asked: 2020-07-30 15:45:23 -0600

Seen: 717 times

Last updated: Aug 05 '20