Question on PSSE terminology
Can someone explain the term ZSORCE, XTRAN, GENTAP please?
First time here? We are a friendly community of Power Systems Engineers. Check out the FAQ!
Can someone explain the term ZSORCE, XTRAN, GENTAP please?
For a synchronous generator XSORCE is the subtransient reactance, Xd”.
XTRAN and GENTAP are only used if the step-up transformer is not modelled in load flow, i.e. the generator is connected directly at the high tension side.
Using XTRAN and GENTAP means you are modeling the generator step-up transformer implicitly (i.e. unit-connected). See the Program Operation Manual for more information.
p.u Generator Dynamic Impedance, ZSORCE p.u. impedance XTRAN = RT, XT on machine MVA base p.u. off-nominal turns ratio (GENTAP) entered in the machine impedance