Two Winding Transfomer

asked Jul 7 '0

EM gravatar image

On Two Winding Transformer, can anyone explainto me what it means, on Control Data, R1max and R1min? What is the difference between Vmax and Vmin?

2 answers

Sort by » oldest newest most voted
1

answered Jul 8 '0

lmcqueen gravatar image

Section 4.4.3 Chapter 4 of PAGV1.pdf documentation explains the Two Winding Transformer PSS/E data entry. It includes calculation of off nominal tap ratios which has something to do with the parameters mentioned. Also you may want to check modeling of Phase Shifting Transformers as it also share the above parameter category with ordinary transformer (i.e. Vmax/Vmin may be p.u. voltage or active power in MW and R1max/R1min may be p.u. ratio or phase angle in degrees).

link
0

answered Jul 9 '0

perolofl gravatar image

A short answer: R1max and R1min are the maximum and minimum ratio for the tap changer side.

Vmax and Vmin specify the voltage dead-band for tap changer control.

link