Two Winding Transfomer
On Two Winding Transformer, can anyone explainto me what it means, on Control Data, R1max and R1min? What is the difference between Vmax and Vmin?
First time here? We are a friendly community of Power Systems Engineers. Check out the FAQ!
On Two Winding Transformer, can anyone explainto me what it means, on Control Data, R1max and R1min? What is the difference between Vmax and Vmin?
A short answer: R1max and R1min are the maximum and minimum ratio for the tap changer side.
Vmax and Vmin specify the voltage dead-band for tap changer control.
Section 4.4.3 Chapter 4 of PAGV1.pdf documentation explains the Two Winding Transformer PSS/E data entry. It includes calculation of off nominal tap ratios which has something to do with the parameters mentioned. Also you may want to check modeling of Phase Shifting Transformers as it also share the above parameter category with ordinary transformer (i.e. Vmax/Vmin may be p.u. voltage or active power in MW and R1max/R1min may be p.u. ratio or phase angle in degrees).
Asked: 2020-07-07 02:18:02 -0500
Seen: 1,695 times
Last updated: Jul 09 '20
what is the difference between the connection code CC=2 and CC=17 for a three winding transformer?
HOW TO CALCULATE FVSI FROM DYNAMIC SIMULATION
Pelec calculation based on Efd
Generator internal voltage, retrieve
Dynamics voltage violation checks
Confusion around base kV and PU voltage