Short circuit study of wind/ solar plant connected to infinite bus

asked May 27 '0

Vikas07 gravatar image

updated May 28 '0

To calculate fault level at different buses in the plant network. How to model infinite bus generator to represent SCR and X/R ratio. Also whether short cicruit impedances are required for infinite bus generator and what to consider? Thanks in advance

1 answer

Sort by » oldest newest most voted
0

answered Jun 3 '0

Jorge gravatar image

Hi, in this case you would have to place a line between the infinite busbar and the following bus. With this in mind, then you would have to calculate the grid impedance by using the short circuit power and the X/R ratio at the connection point. Finally, you would have to set the calculated R and X values (in p.u.) onto the line impedance data.

Hope that helps.