Ask Your Question
1

How Mbase(MVA) is calculated in .raw file

asked 2020-05-27 07:41:34 -0500

dennis_1234 gravatar image

Hi all,

I am adding new machine and I don't know how to choose Mbase (MVA) in the .raw file (under the tab "Machine").

I was given this .raw file that I am working with and the existing Mbase (MVA) for other machines there are different, some are 120MVA, 25MVA, 10MVA etc.

So my question is how this Mbase (MVA) value is calculated/obtained?

The system base in 100MVA

Best regards, A beginner in PSSE

edit retag flag offensive close merge delete

1 answer

Sort by ยป oldest newest most voted
0

answered 2020-05-27 09:33:32 -0500

perolofl gravatar image

Mbase is the rated MVA power for the machine. It is one of the most basic data for a generator, so the information should be available for existing generators.

It is only used for short circuit calculations and dynamic simulations. You can ignore Mbase if you are just doing load flow calculations.

edit flag offensive delete link more

Comments

Thanks alot! I got a little confused by the word "base" before but now I understand it after reading your answer.

dennis_1234 gravatar imagedennis_1234 ( 2020-05-27 14:52:34 -0500 )edit

Your Answer

Please start posting anonymously - your entry will be published after you log in or create a new account.

Add Answer

[hide preview]

Question Tools

1 follower

Stats

Asked: 2020-05-27 07:41:34 -0500

Seen: 1,203 times

Last updated: May 27 '20