0

In line fault

Hello

Does ASCC not do in line fault? only does scmu do in line fault? how to show the scmu results in the diagram? how can I represent an in line fault in the diagram?

roliveira's avatar
1
roliveira
asked 2020-05-09 13:41:04 -0500
edit flag offensive 0 remove flag close merge delete

Comments

add a comment see more comments

2 Answers

0

You can make line tap (LTAP) and insert a dummy bus at the location of the in-line fault, and show the ASCC results in the diagram.

perolofl's avatar
3.8k
perolofl
answered 2020-05-12 10:36:52 -0500
edit flag offensive 0 remove flag delete link

Comments

add a comment see more comments
0

Thank you

People like me who like show results In diagram Im thinking of create a Python script to insert a dummy bus automatically Is possible?

roliveira's avatar
1
roliveira
answered 2020-05-12 16:07:15 -0500, updated 2020-05-12 16:09:47 -0500
edit flag offensive 0 remove flag delete link

Comments

Yes, it is possible. Almost Everything you can do in PSSE can also be done in a Python script.

perolofl's avatar perolofl (2020-05-19 15:53:26 -0500) edit

Thank you very much

roliveira's avatar roliveira (2020-05-22 02:28:52 -0500) edit