Ask Your Question
0

Am i able to change load values and some machine characteristics during a dynamic simulation ?

asked 2020-04-14 13:01:42 -0500

Diogo Carrilho gravatar image

updated 2020-04-14 13:05:22 -0500

So, im a 5th grade student in Eletrical Engeniering course and i have been testing the capability of an windturbine to control frequency and voltage of a determinated bus. For that purpose, i need to know if i am able to change load values and some machine caracteristics during a dynamic simulation. Thanks for the help :)

edit retag flag offensive close merge delete

1 answer

Sort by ยป oldest newest most voted
0

answered 2020-04-15 04:37:03 -0500

perolofl gravatar image

Yes, it is possible to change parameters, e.g. CON setting, during a dynamic simulation. The loading of a wind generator may be changed by updating a proper VAR which contains the value of the turbine power or a voltage control setpoint.

edit flag offensive delete link more

Comments

Thank you for the help kind sir !

Diogo Carrilho gravatar imageDiogo Carrilho ( 2020-04-15 12:20:21 -0500 )edit