WHY 'CLODAL' cannot used all load
Hi,bro, When I simulation with complex load model for every load,which include 50% induction load and 50% constant power load,it was report an error " 'CLODAL 'can not used all load", who can tell me why?
First time here? We are a friendly community of Power Systems Engineers. Check out the FAQ!
Hi,bro, When I simulation with complex load model for every load,which include 50% induction load and 50% constant power load,it was report an error " 'CLODAL 'can not used all load", who can tell me why?
Consider posting such CLOD dyr entry to check for errors. Many times load dynamic models do not work well with loads at a bus with very low voltage (Vpu > 0.98 recommended) or with non-realistic load (genetted generation, very low power factor, Only-Q loads,...). You can test your CLODAL model on the 'savnw.sav' case (located in the example folder of the PSSe installation directory).