Error and suspect during initialization
Anyone knows what does the following initialization error message means and how to fix it? And why sometimes after a few iterations or further down the dynamic simulation steps, the initialization would disappear?
*****ZPSS2A AT BUS:20691 MACH 1  :
 Machine in Synch Comp mode - KS1 set to zero 
*****ZPSS2A AT BUS:20692 MACH 2  :
 Machine in Synch Comp mode - KS1 set to zero 
*****WSTAB4 AT BUS:44281 MACH 1  :
 Machine in Synch Comp mode - Kx set to zero 
 ERROR: PELEC outside LUT range
 MODE = 1
 VREF(I) = 0.9861
 STATEs =    0.986   0.986   1.039   3.842   3.842   1.614   3.788   3.788
 
 
 
 
Are the generators in synchronous generator mode, i.e. Pgen=0?
Yes, the generator output is very close to zero, but not the reactive power output (around 2MVAR from 42.5MVA base machine). What do you reckon the problem is?