PV and WTG Step Change
How to implement step change on PV and WTG 2nd generation dynamic models? Is it only by changing the values of vref and Pref?
First time here? We are a friendly community of Power Systems Engineers. Check out the FAQ!
How to implement step change on PV and WTG 2nd generation dynamic models? Is it only by changing the values of vref and Pref?
I have created a tool named "DMView" to run voltage response test including voltage step change test.
You can download and try it: https://sites.google.com/view/dmview/home%3C/p%3E (https://sites.google.com/view/dmview/home)
Take a look at the VARs available in the reeca, reecb, reecc models. Changing those VARs can be used to stimulate a step change for getting response for the renewable models. If the VARs are not available, you can always write a machine model that changes the wpcmd, wqcmd to get your desired simulation response.
An equivalent approach is to change network voltage and/or frequency at the POI (point of interconnection). Use the playback model PLBVFU1 to run such simulations. Check the posting "PLBVFU1 Playback model" for more info, and the PTI manual, Models -> Generator.
Asked: 2018-12-20 00:33:04 -0500
Seen: 1,470 times
Last updated: Jan 29 '19
Short Circuit Current Use psse dynamic simulation and IEC module (psse34)
Minimum Three-Phase Fault Admittance
How to incorporate economic load dispatch information in PV analysis
Is there any control mechanism for Solar PV generator like PSS for Synchronous Generator?
Why don't you try that and find out if it works?
it's not working.