Line closure distribution factor-PSS/E
Does anyone know PSS/E can calculate Line closure distribution factor(LCDF) or Line outage distribution factor(LODF)? or how can use OTDF to transfer? Thanks!
First time here? We are a friendly community of Power Systems Engineers. Check out the FAQ!
Does anyone know PSS/E can calculate Line closure distribution factor(LCDF) or Line outage distribution factor(LODF)? or how can use OTDF to transfer? Thanks!
I have found that looping through the contingencies in the .acc file, then looping through the branches for each contingency, then comparing to the "BASE CASE" contingency is the best approach. if you find that one of the distribution factors satisfies some criteria, then you can do what you like with the branch, outage, flow, df, information. (version 34) Here is a snippet that effectively does this. 3phaseee.com
# -- GET CONTINGENCY LABELS, BRANCHES AND BUSES FROM SUMMARY ------------------------------
accobject = arrbox.accc_pp.CONTINGENCY_PP(n1accfnames[j])
accsummary = accobject.summary()
conlabels = accsummary.colabel
branches = list(accsummary.melement)
buses = list(accsummary.mvbuslabel)
# -- GET N-0 RESULTS ----------------------------------------------------------------------
n0results = accobject.solution('BASE CASE')
n0volts = n0results.volts
n0flows = list(n0results.ampflow)
# -----------------------------------------------------------------------------------------
# -- CHECK N-1 RESULTS FOR IMPACTED BUSES AND BRANCHES ------------------------------------
# -----------------------------------------------------------------------------------------
for prilabel in conlabels[1:]:
results = accobject.solution(prilabel)
pridesc = list(results.codesc)
n1volts = results.volts
n1flows = list(results.ampflow)
if not results.cnvflag: continue
for f in range(len(branches)):
getcon = False
if n1flows[f] == 0.0:
continue
df = abs((n1flows[f] - n0flows[f]) / n0flows[f])
if df > screenDF:
getcon = True
if not getcon:
getcon = True in [abs(n1volts[v] - n0volts[v]) > screenVF for v in range(len(buses))]
if getcon: ....................
A good discussion about these linear factors can be found at "https://www.powerworld.com/files/TrainingI11LinearAnalysis.pdf"
does someone have a related python code, besides the "sensitivity_factors.py" posted at the example folder?
Asked: 2018-10-30 03:17:36 -0500
Seen: 1,452 times
Last updated: Oct 30 '18
Can someone share the original IEEE 14,24 or 39 bus systems data?
How to save a value in fortran and re-use it ?
Is it possible to create a .dyr file with just the model data for a turbine/generator?
How does PSSE file match real-time branch flow measurements?
PSSE output not always going to directed output file
Change all buses load P and Q injections
whit loves you. Content on this site is licensed under a Creative Commons Attribution Share Alike 3.0 license.