Ask Your Question
0

Network does not converge due to large amount of CLMDBLU2 in system

asked 2017-11-21 18:41:08 -0600

Phyl gravatar image

Hi All,

I am using version PSS/E 34.2 to do dynamic simulations. I am including a high amount of CLMDBLU2 load models, and when the percentage of loads with load models that I include in the dynamic file increases above 25% I receive the error that the network does not converge. All my dynamic models have been checked with DOCU, and there aren't any problems. I am unsure of why I am getting the error. Any suggestions appreciated.

Thanks!

edit retag flag offensive close merge delete

2 answers

Sort by » oldest newest most voted
0

answered 2017-11-28 03:16:54 -0600

perolofl gravatar image

I assume you are simulating a disturbance when you get network does not converge. If so, there might be a voltage stability problem when using a high amount of dynamic load models.

Please elaborate more on when the problem occurs in the simulation. Is it after fault insertion?

edit flag offensive delete link more

Comments

The network does not converge after initialization once the simulation is running during the first time step. This is prior to any fault insertion.

Phyl gravatar imagePhyl ( 2017-11-30 11:59:17 -0600 )edit

This error also occurs with any test system that I use regardless of the size of the system, the error happens when between 25% and 50% of the loads are CLMDBLU2. This does not occur when I use other models such as CLODBL.

Phyl gravatar imagePhyl ( 2017-11-30 13:46:08 -0600 )edit

Run just 1 time step and check the voltages. Use activity DIFF (File - Compare - Powerflow Cases) to compare the actual bus voltages with the original voltages in the saved case. I guess you have problem at some load buses.

perolofl gravatar imageperolofl ( 2017-12-01 06:30:27 -0600 )edit

I've used DIFF and there are several buses where there are difference between the actual and original bus voltages. Do you have a suggestion for what to change in model to remedy this?

Phyl gravatar imagePhyl ( 2017-12-04 19:46:01 -0600 )edit

You are using a very complicated load model at many load buses. How did you get all the parameters? DOCU,CHECK is not a gaurantee of correct or decent parameters. It seems to be a nightmare to use that model. I recommend to switch to another model.

perolofl gravatar imageperolofl ( 2017-12-05 01:35:54 -0600 )edit
0

answered 2017-11-22 06:16:54 -0600

jconto gravatar image

Check the Program Operation Manual, Chp. 3, Table 3-1. Standard Maximum PSS®E Program Capacities Your set up might be exceeding PSSe vars dimensions.

edit flag offensive delete link more

Comments

If so it would have been alarmed at DYRE and the exceeding models would be ignored. It can hardly be the reason for network not converging.

perolofl gravatar imageperolofl ( 2017-11-28 03:19:24 -0600 )edit

I have checked with the POM and I am not exceeding any limits as I am using the 200,000 bus size level.

Phyl gravatar imagePhyl ( 2017-11-30 12:12:53 -0600 )edit

Your Answer

Please start posting anonymously - your entry will be published after you log in or create a new account.

Add Answer

[hide preview]

Question Tools

1 follower

Stats

Asked: 2017-11-21 18:41:08 -0600

Seen: 1,559 times

Last updated: Nov 28 '17