CLOD model in PSS/E
I need to know the capacity of large and small motors in the CLOD model? Can I change it? Thanks.
First time here? We are a friendly community of Power Systems Engineers. Check out the FAQ!
Yes Brother! u can change the CLOAD model Parameters. But sum of the all percentages must be remain 100. For Example;
For Industrial Zones
Large Motors 5 % Small Motors 50 % Transformer Exciting Current 1 % Discharge Lighting 15 % Constant Power 10 % Constant Impedance 19 % Check from Above Data sum is equal to 100 %
According to Zones Type these parameters can be changed .